Im new to signalling and new to the railway. Just wondering how are DC track circuit powered. What are the fault indication if current, resistance or voltage were higher than normal?
Posts: 44
Threads: 2
Joined: Feb 2008
Reputation:
3
It's worth adding that almost universally today, a "DC" track circuit is powered by a transformer-rectifier set from a 110V AC supply. As there is a separate unit for each track circuit, this creates a "virtual battery" for each track circuit, electrically isolated from all others. The "DC" voltage will therefore actually be full-wave-rectified AC and so very lumpy compared to true DC, but the relay only cares about the mean DC level.
It would be perfectly possible to create a microprocessor-controlled track circuit with the ability to self-adjust for changing conditions or to report faults through a serial link, but this option isn't used in the UK.
I do seem to recall (i reserve the right to be wrong here!) that the new digital TI21 track circuit (EBI track 200) has some sort of self-diagnostic capability. I've also encountered the AF902 track circuit (former US&S product, now Ansaldo STS), which is microprocessor controlled and can interface to the interlocking through a serial link, so this also has that potential. It's not used in the UK.
reuben